The issue with translating fuse links to fuses is ampacity. Fuses rate wires by ampacity, fusible links you just choose the one two gauges smaller.
If you wanted to do it correctly, you'd have to calculate the maximum current carrying capacity of the wire, which has to take into account the gauge, the voltage AND the length (and if you want to get super precise, the ambient temperature and wire temperature). That's the shortcoming of most internet 12v wiring charts. There are nine million of them, and all have a different opinion on what the proper ampere rating of a wire is.
The info that OldBull provided is the best way to set the system up. If the load current of a single plug is approximately 30 amperes, then you could fuse each bank separately, to avoid using 8 fuses. So, a 130 ampere ATM fuse would probably be fine. But that brings up another issue. If you do it that way, and run a #10 wire to each plug from the fuse, then those #10 wires are not properly protected. Are they protected well enough? Most likely. But, if one plug fails (open circuit, no current in that wire), and then let's say another fails shorted. That wire will be allowed to carry 60 amperes for a small period of time until the ATM fuse blows. Is it long enough to catch fire? I wouldn't bet on it. Still, the way that it's protected from the factoury is, IMHO, the best way to protect the plugs.
All of that being said, I will probably be adding two Mini-ANL fuses to mine, one for each bank, and keeping the fuse links. That way my main feed wires are protected, as well as each individual wire.
/electrical rant