Well, that was a failed experiment... Stick thermometers don't work... Even if you wrap the pipe with foam insulation for the purpose of deflecting the hot air from the exposed stem... Then I tried a thermocouple from one of those indoor-outdoor digital thermometers... I shoved the thermocouple into the space between the pipe insulation and the tube just before it goes to the accumulator, where the low side pressure readings are taken....
@ 30 PSI, the temp should have been 18°, according to the P/T chart for the refrigerant I'm using... With the thermocouple, I got 55°... Stuffed into the tight space between the tube and the inside of the pipe insulation... Argg... How can the vent temp be 45° when the temp measured by this thermocouple says 55°?
Ok, let's summarize... The evaporator inlet tube is slightly icing up just past the orifice tube...And that's with the cycle switch set to cycle off at 30 PSI.
With the IR thermometer at the evaporator outlet, before it goes into the accumulator, the temp is 25°, but not frosting up...
For what it's worth, the IR thermometer, when taking temp reading at wall thermostat in house, reads 65° when the wall thermostat reads 74° and it's digital...
So, if the IR thermometer is 9° colder than actual reading, then that means
those temp readings I gave earlier needs to be corrected by adding 9°...
That sounds about right...
But the low-side pressure reading is taken at the evap outlet. I recorded 30 PSI and the corrected temp would be 34°... But it's supposed to be 18° at that pressure...
Either my gauges are off, or the Pressure/Temperature Chart for this refrigerant is wrong... Here is the P/T chart.
You must be registered for see images attach
This does not compute... How can you get 34° @ 30PSI, when it's supposed to be 18°?
I tried to do everything by the numbers and something is whacked badly... Very frustrating... I'd appreciate anybody's thoughts, if they can see where this went wrong...
I know that some air in the system would result in diluted charge and skew the P/T relationship, but when I charged this sucker up the first time, I did so from a hard vacuum that held for one hour and then I hooked the charging hose to the first can and purged the hose with the can upside down, so that liquid would purge out and there would be no air in the hose.
I had left the hose adapters that enables me to hook my R-132a gauges to the R-12 connections and it leaked overnight. When I discovered that it leaked some of the charge (it still had 35 PSI @ 70°) I made sure I thoroughly purged the charging (yellow) and the low-side hoses before I allowed the charge to enter the system.
Anyway, I said all of that to show that there can't be any air in the system. It still had 35 PSI and I purged the hoses... Ergo, no air...
I see Itsacrazyasian is here... Yeah, I installed a ball valve set up to divert the hot water away from the heater core... And it's diverting... Do you suppose that, no, there's no way ball valves can leak that soon... It's only two years old...